cabinet Bob posted:
Bill_R posted:

A    you will need 2400 watts worth of LED's before you trip a 20 amp breaker.         Ia=2400w/120v = 20 amps. You can not consider secondary current  when determining primary over current protection,  only watts  

B   power factor, applied power (VA),  eddy currents, power factor or phase angle (one in the same) these are toys not real factorys, not applicable !.

I am a EE and in the electrical construction business for 25 years

Thanks Bill ! So are you saying, I'm  ok with what I have ? Bob

 

Absolutely 