Skip to main content

I redid my layout and I’m testing voltage before I put any engines on the track.  I’m using a PH180 for track power and a Z1000 (accessory) for DZ2500’s.  Both transformers use the same outlet.  They are on same phase.    I have one common under the layout that both track and switches are tied into.

my question is there are some areas where I have 12.5 volts. This is where I put the volt meter probes on the center rail and the isolated rail that’s used for non derailing for the 2500’s. I don’t know if this is a problem or not.

Original Post

Replies sorted oldest to newest

Sounds like voltage loos due to poor electrical distribution throughout the layout. A few tips:

  • Be sure to use the proper wire type and size for the application. Generally 14AWG is recommended for the bus runs and 16AWG for local drops.
  • Make sure you have multiple drops to the track. Track joints are well known to inhibit the flow of electricity and so having drops/feeders every few sections of track is recommended
  • Be sure you have multi-meter that can read the true RMS Voltage of an electronic AC waveform.
  • Look into adequate subcircuit protections with strategically sized and placed instant circuit breakers and TVS diodes. (This won't help with your voltage drop question, but part of a good layout electrical distribution plan)

Don't measure from the non-derailing rail, that's not a useful measurement.  You're really measuring the internal circuitry that senses the wheels conducting from the opposite rail.  Ignore that reading and move on.

Ok thanks.  I wasn’t sure if that was a concern or not.

I am using 14 gauge bus with drops every 6 feet.  I don’t have any voltage drops, it’s just lower across the isolated sections for non derailing.

Add Reply

Post

OGR Publishing, Inc., 1310 Eastside Centre Ct, Suite 6, Mountain Home, AR 72653
800-980-OGRR (6477)
www.ogaugerr.com

×
×
×
×
Link copied to your clipboard.
×
×