Skip to main content

I would like to add an on/off switch to the power cord to of the ZW275 to make it easy to access on my control panel. The PO added a new power cord and the cord has one line ribbed. But the plug end has two small blades (re, no wide blade on the ribbed line). Does it matter which line I cut to install the switch?

Thanks for the help.

Attachments

Images (3)
  • control panel
  • cord
  • on-off switch
Original Post

Replies sorted oldest to newest

WftTrains posted:

Rather than cutting the cord, why not spend a few bucks on a remote-controlled on-off switch.  You can wear the switch around your neck on a lanyard and it then also serves as a panic or emergency shut-off switch.  They were less than $10 the last time I bought one. 

Bill

 

cool idea. I will have to find one up.

BackYardBill posted:
WftTrains posted:

Rather than cutting the cord, why not spend a few bucks on a remote-controlled on-off switch.  You can wear the switch around your neck on a lanyard and it then also serves as a panic or emergency shut-off switch.  They were less than $10 the last time I bought one. 

Bill

 

cool idea. I will have to find one up.

Bill:

Here's a link to the one I recently bought at Lowe's: https://www.lowes.com/pd/Utilitech-Black/3798937

Note that it has two outlets so you can plug two transformers into it if you need to.

Bill

Last edited by WftTrains

Bill the resistive rating for the remote on/off outlet is 13A/1625W and the tungsten rating is 8A/1000W so NO I wouldn't use it with a ZW.  Its intended purpose is for plug in lighting such a table lamps, security lighting, landscape lighting and Christmas lighting.  As others have said your best bet is to use a good power strip.

remote

Attachments

Images (1)
  • remote
Last edited by wild mary

The 275 watts is input, so that's about 2.3 amps ac thru the cord. As for the suggested remote switches, any of them would be fine. I been using that black remote suggested above for several years to power up a ZW-C with four bricks. I think the tungsten rating on that remote switch is lower because of the surge of amps into a cold tungsten filament. As to the inductive load of a transformer, I think it has some back emf issues when switching off, but the rating seems ample.